Discussion:
Two stage furnaces and thermostats
(too old to reply)
d***@krl.org
2011-12-25 21:29:36 UTC
Permalink
My LPG furnace developed a heat exchanger leak and so it has been
replaced with a high efficiency two stage furnace. The old furnace
was also a high efficiency furnace but just a one stage 100k BTU/
hour. The replacement is a 90k btu/hr / 63k btu/hr. Did not do a
proper analysis of the size furnace needed, but based on how the new
furnace seems to be working, the low stage is good to below 20 degrees
F. right now. And I am going to put in more insulation so things
will change a little. The new furnace has jumper settings for using
a one stage thermostat with 5 or 12 minutes wait before kicking in to
high, or for using a two stage thermostat.

Okay here is the question...........it seems to be that the furnace
ought to run at the low stage unless the outside temperature is below
about 20 degrees F. Then switch to high stage as long as the outside
temperature is below 20 degrees. There is no mention of doing this in
the furnace manual. So is this a bad idea for some reason.

It seems like a simple thermal switch located outside would be better
than spending a bundle on a two stage thermostat.


Dan
Steve
2011-12-26 01:54:23 UTC
Permalink
Post by d***@krl.org
My LPG furnace developed a heat exchanger leak and so it has been
replaced with a high efficiency two stage furnace. The old furnace
was also a high efficiency furnace but just a one stage 100k BTU/
hour. The replacement is a 90k btu/hr / 63k btu/hr. Did not do a
proper analysis of the size furnace needed, but based on how the new
furnace seems to be working, the low stage is good to below 20 degrees
F. right now. And I am going to put in more insulation so things
will change a little. The new furnace has jumper settings for using
a one stage thermostat with 5 or 12 minutes wait before kicking in to
high, or for using a two stage thermostat.
Okay here is the question...........it seems to be that the furnace
ought to run at the low stage unless the outside temperature is below
about 20 degrees F. Then switch to high stage as long as the outside
temperature is below 20 degrees. There is no mention of doing this in
the furnace manual. So is this a bad idea for some reason.
It seems like a simple thermal switch located outside would be better
than spending a bundle on a two stage thermostat.
Dan
Keep it simple.... use a 2 stage thermostat, and don't bother with the
jumper settings. that way it will only give you what heat that the
thermostat calls for.
i***@gmail.com
2011-12-26 16:08:41 UTC
Permalink
Post by d***@krl.org
My LPG furnace developed a heat exchanger leak and so it has been
replaced with a high efficiency two stage furnace.  The old furnace
was also a high efficiency furnace but just a one stage 100k BTU/
hour.   The replacement is a 90k btu/hr /  63k btu/hr.  Did not do a
proper analysis of the size furnace needed,  but based on how the new
furnace seems to be working, the low stage is good to below 20 degrees
F.  right now.  And I am going to put in more insulation so things
will change a little.   The new furnace has jumper settings for using
a one stage thermostat with 5 or 12 minutes wait before kicking in to
high, or for using a two stage thermostat.
Okay here is the question...........it seems to be that the furnace
ought to run at the low stage unless the outside temperature is below
about 20 degrees F.  Then switch to high stage as long as the outside
temperature is below 20 degrees.  There is no mention of doing this in
the furnace manual.  So is this a bad idea for some reason.
It seems like a simple thermal switch located outside would be better
than spending a bundle on a two stage thermostat.
Dan
Dan, Generally speaking...it is better to operate from space demand
which is directly linked to heat loss from the structure ...so, if
you get full sunny days during the winter you can take advantage of
the solar heat coming thru windows as well as heat produced within
the house from food cooking, showers , etc... which *may keep you on
first stage furnace operation longer thereby maximizing economy .
This is the advantage of using a 2 stage space thermostat , whereas
if you go the outdoor thermostat route you are basing operation on
the outdoor temperature without considering possible heat generation
within the house and from the sun . So, my vote is for you to go
with true 2-stage heat operation via a 2 stage electronic
programmable thermostat and hook it up to the furnace control board
in like manner .
d***@krl.org
2011-12-29 22:07:50 UTC
Permalink
Dan,  Generally speaking...it is better to operate from space demand
which is directly linked to heat loss from the structure ...so,  if
you get full sunny days during the winter you can take advantage of
the solar heat coming thru windows  as well as heat produced within
the house from food cooking, showers , etc... which *may keep you on
first stage furnace operation longer thereby maximizing  economy .
This is the advantage of using a 2 stage space thermostat  , whereas
if you go the outdoor thermostat route you are basing operation  on
the outdoor temperature without considering possible heat generation
within the house and from the sun  .   So, my vote is for you to go
with  true 2-stage heat operation via a 2 stage electronic
programmable thermostat  and hook it up to the furnace control board
in like manner .
You did bring up a good point. If it is sunny the house will stay
warm without running the furnace when the temperature is forty
degrees. If I do go the outside temperature switch I will put it in a
box that has some solar gain built into it. My big problem with two
stage thermostats is they seem to be very expensive. I may not be
looking in the right places, but most of the two stage thermostats at
Grainger are 200 + dollars. ( they do have some that are a little over
50 dollars. )

Dan
Steve
2011-12-29 23:13:08 UTC
Permalink
Dan, Generally speaking...it is better to operate from space demand
which is directly linked to heat loss from the structure ...so, if
you get full sunny days during the winter you can take advantage of
the solar heat coming thru windows as well as heat produced within
the house from food cooking, showers , etc... which *may keep you on
first stage furnace operation longer thereby maximizing economy .
This is the advantage of using a 2 stage space thermostat , whereas
if you go the outdoor thermostat route you are basing operation on
the outdoor temperature without considering possible heat generation
within the house and from the sun . So, my vote is for you to go
with true 2-stage heat operation via a 2 stage electronic
programmable thermostat and hook it up to the furnace control board
in like manner .
You did bring up a good point. If it is sunny the house will stay
warm without running the furnace when the temperature is forty
degrees. If I do go the outside temperature switch I will put it in a
box that has some solar gain built into it. My big problem with two
stage thermostats is they seem to be very expensive. I may not be
looking in the right places, but most of the two stage thermostats at
Grainger are 200 + dollars. ( they do have some that are a little over
50 dollars. )

Dan

Honeywell FocusPro 5000 TH5220D1003
i***@gmail.com
2012-01-03 15:20:22 UTC
Permalink
Dan,  Generally speaking...it is better to operate from space demand
which is directly linked to heat loss from the structure ...so,  if
you get full sunny days during the winter you can take advantage of
the solar heat coming thru windows  as well as heat produced within
the house from food cooking, showers , etc... which *may keep you on
first stage furnace operation longer thereby maximizing  economy .
This is the advantage of using a 2 stage space thermostat  , whereas
if you go the outdoor thermostat route you are basing operation  on
the outdoor temperature without considering possible heat generation
within the house and from the sun  .   So, my vote is for you to go
with  true 2-stage heat operation via a 2 stage electronic
programmable thermostat  and hook it up to the furnace control board
in like manner .
You did bring up a good point.  If it is sunny the house will stay
warm without running the furnace when the temperature is forty
degrees.  If I do go the outside temperature switch I will put it in a
box that has some solar gain built into it.  My big problem with two
stage thermostats is they seem to be very expensive.  I may not be
looking in the right places, but most of the two stage thermostats at
Grainger are 200 + dollars. ( they do have some that are a little over
50 dollars.  )
                                               Dan
Youre going to spend close to that regardless of what 2 stage
programmable stat you go with. . If you want to go the cheap route,
then your outdoor stat idea would be better than nothing.
Steve
2012-01-03 16:37:45 UTC
Permalink
Dan, Generally speaking...it is better to operate from space demand
which is directly linked to heat loss from the structure ...so, if
you get full sunny days during the winter you can take advantage of
the solar heat coming thru windows as well as heat produced within
the house from food cooking, showers , etc... which *may keep you on
first stage furnace operation longer thereby maximizing economy .
This is the advantage of using a 2 stage space thermostat , whereas
if you go the outdoor thermostat route you are basing operation on
the outdoor temperature without considering possible heat generation
within the house and from the sun . So, my vote is for you to go
with true 2-stage heat operation via a 2 stage electronic
programmable thermostat and hook it up to the furnace control board
in like manner .
You did bring up a good point. If it is sunny the house will stay
warm without running the furnace when the temperature is forty
degrees. If I do go the outside temperature switch I will put it in a
box that has some solar gain built into it. My big problem with two
stage thermostats is they seem to be very expensive. I may not be
looking in the right places, but most of the two stage thermostats at
Grainger are 200 + dollars. ( they do have some that are a little over
50 dollars. )
Dan
Youre going to spend close to that regardless of what 2 stage
programmable stat you go with. . If you want to go the cheap route,
then your outdoor stat idea would be better than nothing.



------------------------------------------------

The Honeywell 2 stage stat I posted( Honeywell FocusPro 5000 TH5220D1003) is
around $50 and will do the job. It will be less expensive and less of a PITA
than running new wires and buying another stat and OD temp sensor that will
support balance point operation.
i***@gmail.com
2012-01-03 20:12:05 UTC
Permalink
Post by i***@gmail.com
Dan, Generally speaking...it is better to operate from space demand
which is directly linked to heat loss from the structure ...so, if
you get full sunny days during the winter you can take advantage of
the solar heat coming thru windows as well as heat produced within
the house from food cooking, showers , etc... which *may keep you on
first stage furnace operation longer thereby maximizing economy .
This is the advantage of using a 2 stage space thermostat , whereas
if you go the outdoor thermostat route you are basing operation on
the outdoor temperature without considering possible heat generation
within the house and from the sun . So, my vote is for you to go
with true 2-stage heat operation via a 2 stage electronic
programmable thermostat and hook it up to the furnace control board
in like manner .
You did bring up a good point. If it is sunny the house will stay
warm without running the furnace when the temperature is forty
degrees. If I do go the outside temperature switch I will put it in a
box that has some solar gain built into it. My big problem with two
stage thermostats is they seem to be very expensive. I may not be
looking in the right places, but most of the two stage thermostats at
Grainger are 200 + dollars. ( they do have some that are a little over
50 dollars. )
Dan
Youre going to spend close to that regardless of what 2 stage
programmable stat you go with.  . If you want to go the cheap route,
then your outdoor stat idea would be better than nothing.
------------------------------------------------
The Honeywell 2 stage stat I posted( Honeywell FocusPro 5000 TH5220D1003) is
around $50 and will do the job. It will be less expensive and less of a PITA
than running new wires and buying another stat and OD temp sensor that will
support balance point operation.
Well, if he can get a 2 stage stat for $50 , then absolutely that is
the way to go. Ive never seen one that cheap.
d***@krl.org
2012-01-03 21:49:32 UTC
Permalink
Post by i***@gmail.com
Post by i***@gmail.com
Youre going to spend close to that regardless of what 2 stage
programmable stat you go with.  . If you want to go the cheap route,
then your outdoor stat idea would be better than nothing.
------------------------------------------------
The Honeywell 2 stage stat I posted( Honeywell FocusPro 5000 TH5220D1003) is
around $50 and will do the job. It will be less expensive and less of a PITA
than running new wires and buying another stat and OD temp sensor that will
support balance point operation.
Well, if he can get a 2 stage stat for $50 , then absolutely that is
the way to go.  Ive never seen one that cheap.
Ah, the Honeywell FocusPro is not programmable. I am amazed at how
much two stage thermostats cost. I would think that there would be
lots of models using a relatively cheap micro-controler.

Dan
Steve
2012-01-03 23:36:52 UTC
Permalink
Post by i***@gmail.com
Post by i***@gmail.com
Youre going to spend close to that regardless of what 2 stage
programmable stat you go with. . If you want to go the cheap route,
then your outdoor stat idea would be better than nothing.
------------------------------------------------
The Honeywell 2 stage stat I posted( Honeywell FocusPro 5000
TH5220D1003) is
around $50 and will do the job. It will be less expensive and less of a PITA
than running new wires and buying another stat and OD temp sensor that will
support balance point operation.
Well, if he can get a 2 stage stat for $50 , then absolutely that is
the way to go. Ive never seen one that cheap.
Ah, the Honeywell FocusPro is not programmable. I am amazed at how
much two stage thermostats cost. I would think that there would be
lots of models using a relatively cheap micro-controler.

Dan

------------------------------------

Do you want a cheap stat?? or a good one?? In the last couple of months I
have replaced several Lux and Hunter stats that failed because they are
junk. Out of all of the Honeywell stats I have installed, I have only had to
warranty a half dozen. The H'well stats have a 5 year warranty on them too.
Steve
2012-01-03 23:33:58 UTC
Permalink
Post by i***@gmail.com
Dan, Generally speaking...it is better to operate from space demand
which is directly linked to heat loss from the structure ...so, if
you get full sunny days during the winter you can take advantage of
the solar heat coming thru windows as well as heat produced within
the house from food cooking, showers , etc... which *may keep you on
first stage furnace operation longer thereby maximizing economy .
This is the advantage of using a 2 stage space thermostat , whereas
if you go the outdoor thermostat route you are basing operation on
the outdoor temperature without considering possible heat generation
within the house and from the sun . So, my vote is for you to go
with true 2-stage heat operation via a 2 stage electronic
programmable thermostat and hook it up to the furnace control board
in like manner .
You did bring up a good point. If it is sunny the house will stay
warm without running the furnace when the temperature is forty
degrees. If I do go the outside temperature switch I will put it in a
box that has some solar gain built into it. My big problem with two
stage thermostats is they seem to be very expensive. I may not be
looking in the right places, but most of the two stage thermostats at
Grainger are 200 + dollars. ( they do have some that are a little over
50 dollars. )
Dan
Youre going to spend close to that regardless of what 2 stage
programmable stat you go with. . If you want to go the cheap route,
then your outdoor stat idea would be better than nothing.
------------------------------------------------
The Honeywell 2 stage stat I posted( Honeywell FocusPro 5000 TH5220D1003) is
around $50 and will do the job. It will be less expensive and less of a PITA
than running new wires and buying another stat and OD temp sensor that will
support balance point operation.
Well, if he can get a 2 stage stat for $50 , then absolutely that is
the way to go. Ive never seen one that cheap.

--------------------------------------------------

There is a reason I posted that particular model.... Its a good quality
stat, and my customers that have them have been very pleased. You can do a
simple search on yahoo and find a bunch of places that have them for $50 or
less.
It also has an auto-changeover feature.... will change from heat to cool or
vise versa on its own... nice to have in the fall and spring when your
running the a/c during the day and heat at night.
i***@gmail.com
2012-01-04 19:44:13 UTC
Permalink
Post by i***@gmail.com
Post by i***@gmail.com
Dan, Generally speaking...it is better to operate from space demand
which is directly linked to heat loss from the structure ...so, if
you get full sunny days during the winter you can take advantage of
the solar heat coming thru windows as well as heat produced within
the house from food cooking, showers , etc... which *may keep you on
first stage furnace operation longer thereby maximizing economy .
This is the advantage of using a 2 stage space thermostat , whereas
if you go the outdoor thermostat route you are basing operation on
the outdoor temperature without considering possible heat generation
within the house and from the sun . So, my vote is for you to go
with true 2-stage heat operation via a 2 stage electronic
programmable thermostat and hook it up to the furnace control board
in like manner .
You did bring up a good point. If it is sunny the house will stay
warm without running the furnace when the temperature is forty
degrees. If I do go the outside temperature switch I will put it in a
box that has some solar gain built into it. My big problem with two
stage thermostats is they seem to be very expensive. I may not be
looking in the right places, but most of the two stage thermostats at
Grainger are 200 + dollars. ( they do have some that are a little over
50 dollars. )
Dan
Youre going to spend close to that regardless of what 2 stage
programmable stat you go with. . If you want to go the cheap route,
then your outdoor stat idea would be better than nothing.
------------------------------------------------
The Honeywell 2 stage stat I posted( Honeywell FocusPro 5000 TH5220D1003) is
around $50 and will do the job. It will be less expensive and less of a PITA
than running new wires and buying another stat and OD temp sensor that will
support balance point operation.
Well, if he can get a 2 stage stat for $50 , then absolutely that is
the way to go.  Ive never seen one that cheap.
--------------------------------------------------
There is a reason I posted that particular model.... Its a good quality
stat, and my customers that have them have been very pleased. You can do a
simple search on yahoo and find a bunch of places that have them for $50 or
less.
It also has an auto-changeover  feature.... will change from heat to cool or
vise versa on its own... nice to have in the fall and spring when your
running the a/c during the day and heat at night.
I personally think an auto changeover feature on a thermostat for
residential is not a good idea ; it could turn on the a/c in cold
weather and possibily destroy the compressor if there exists
interally generated heat from cooking, many people in the house at one
time, or from a lamp too near the thermostat. Id only go with auto
changeover if there was a low ambient cutout switch on the a/c unit.
Steve
2012-01-04 19:56:57 UTC
Permalink
Post by i***@gmail.com
Post by i***@gmail.com
Dan, Generally speaking...it is better to operate from space demand
which is directly linked to heat loss from the structure ...so, if
you get full sunny days during the winter you can take advantage of
the solar heat coming thru windows as well as heat produced within
the house from food cooking, showers , etc... which *may keep you on
first stage furnace operation longer thereby maximizing economy .
This is the advantage of using a 2 stage space thermostat , whereas
if you go the outdoor thermostat route you are basing operation on
the outdoor temperature without considering possible heat generation
within the house and from the sun . So, my vote is for you to go
with true 2-stage heat operation via a 2 stage electronic
programmable thermostat and hook it up to the furnace control board
in like manner .
You did bring up a good point. If it is sunny the house will stay
warm without running the furnace when the temperature is forty
degrees. If I do go the outside temperature switch I will put it in a
box that has some solar gain built into it. My big problem with two
stage thermostats is they seem to be very expensive. I may not be
looking in the right places, but most of the two stage thermostats at
Grainger are 200 + dollars. ( they do have some that are a little over
50 dollars. )
Dan
Youre going to spend close to that regardless of what 2 stage
programmable stat you go with. . If you want to go the cheap route,
then your outdoor stat idea would be better than nothing.
------------------------------------------------
The Honeywell 2 stage stat I posted( Honeywell FocusPro 5000
TH5220D1003)
is
around $50 and will do the job. It will be less expensive and less of a PITA
than running new wires and buying another stat and OD temp sensor that will
support balance point operation.
Well, if he can get a 2 stage stat for $50 , then absolutely that is
the way to go. Ive never seen one that cheap.
--------------------------------------------------
There is a reason I posted that particular model.... Its a good quality
stat, and my customers that have them have been very pleased. You can do a
simple search on yahoo and find a bunch of places that have them for $50 or
less.
It also has an auto-changeover feature.... will change from heat to cool
or
vise versa on its own... nice to have in the fall and spring when your
running the a/c during the day and heat at night.
I personally think an auto changeover feature on a thermostat for
residential is not a good idea ; it could turn on the a/c in cold
weather and possibily destroy the compressor if there exists
interally generated heat from cooking, many people in the house at one
time, or from a lamp too near the thermostat. Id only go with auto
changeover if there was a low ambient cutout switch on the a/c unit.

---------------------------------------------------------------\


Think 5 degree dead band....
I have been putting in both the FocusPro and the VisionPro for many years...
I have never had a problem with compressors. But then the refrigerant charge
is properly balanced by subcooling and superheat, correctly sized ductwork,
etc.

The only way I can think of that you would have a problem with the a/c
trying to come on in the winter is if the stat is in a closed kitchen when
your doing holiday cooking.... not a good idea
i***@gmail.com
2012-01-04 21:34:31 UTC
Permalink
Post by i***@gmail.com
Post by i***@gmail.com
Post by i***@gmail.com
Dan, Generally speaking...it is better to operate from space demand
which is directly linked to heat loss from the structure ...so, if
you get full sunny days during the winter you can take advantage of
the solar heat coming thru windows as well as heat produced within
the house from food cooking, showers , etc... which *may keep you on
first stage furnace operation longer thereby maximizing economy .
This is the advantage of using a 2 stage space thermostat , whereas
if you go the outdoor thermostat route you are basing operation on
the outdoor temperature without considering possible heat generation
within the house and from the sun . So, my vote is for you to go
with true 2-stage heat operation via a 2 stage electronic
programmable thermostat and hook it up to the furnace control board
in like manner .
You did bring up a good point. If it is sunny the house will stay
warm without running the furnace when the temperature is forty
degrees. If I do go the outside temperature switch I will put it in a
box that has some solar gain built into it. My big problem with two
stage thermostats is they seem to be very expensive. I may not be
looking in the right places, but most of the two stage thermostats at
Grainger are 200 + dollars. ( they do have some that are a little over
50 dollars. )
Dan
Youre going to spend close to that regardless of what 2 stage
programmable stat you go with. . If you want to go the cheap route,
then your outdoor stat idea would be better than nothing.
------------------------------------------------
The Honeywell 2 stage stat I posted( Honeywell FocusPro 5000
TH5220D1003)
is
around $50 and will do the job. It will be less expensive and less of a PITA
than running new wires and buying another stat and OD temp sensor that will
support balance point operation.
Well, if he can get a 2 stage stat for $50 , then absolutely that is
the way to go. Ive never seen one that cheap.
--------------------------------------------------
There is a reason I posted that particular model.... Its a good quality
stat, and my customers that have them have been very pleased. You can do a
simple search on yahoo and find a bunch of places that have them for $50 or
less.
It also has an auto-changeover feature.... will change from heat to cool
or
vise versa on its own... nice to have in the fall and spring when your
running the a/c during the day and heat at night.
I personally think an auto changeover feature on a thermostat for
residential is not a good idea ;  it could turn on the a/c in cold
weather and possibily destroy the compressor  if there exists
interally generated heat from cooking, many people in the house at one
time, or from a lamp too near the thermostat.  Id only go with auto
changeover if there was a low ambient cutout switch on the a/c unit.
---------------------------------------------------------------\
Think 5 degree dead band....
I have been putting in both the FocusPro and the VisionPro for many years...
I have never had a problem with compressors. But then the refrigerant charge
is properly balanced by subcooling and superheat, correctly sized ductwork,
etc.
The only way I can think of that you would have a problem with the a/c
trying to come on in the winter is if the stat is in a closed kitchen when
your doing holiday cooking.... not a good idea
A 5 f. dead band is not adequate protection ; if the heating
setpoint is low like at 65 f. the sun hitting the thermostat
directly or a wood burning fireplace , prolonged oven cooking,
etc...could easily push the temperature to 71 f and higher which would
trigger the mechanical cooling at an outdoor temperature cold enough
to cause equipment harm . Shutting off the a/c breaker is always a
good idea in the winter , regardless .
Steve
2012-01-04 23:14:19 UTC
Permalink
Post by i***@gmail.com
Post by i***@gmail.com
Post by i***@gmail.com
Dan, Generally speaking...it is better to operate from space demand
which is directly linked to heat loss from the structure ...so, if
you get full sunny days during the winter you can take advantage of
the solar heat coming thru windows as well as heat produced within
the house from food cooking, showers , etc... which *may keep you on
first stage furnace operation longer thereby maximizing economy .
This is the advantage of using a 2 stage space thermostat , whereas
if you go the outdoor thermostat route you are basing operation on
the outdoor temperature without considering possible heat generation
within the house and from the sun . So, my vote is for you to go
with true 2-stage heat operation via a 2 stage electronic
programmable thermostat and hook it up to the furnace control board
in like manner .
You did bring up a good point. If it is sunny the house will stay
warm without running the furnace when the temperature is forty
degrees. If I do go the outside temperature switch I will put it in a
box that has some solar gain built into it. My big problem with two
stage thermostats is they seem to be very expensive. I may not be
looking in the right places, but most of the two stage thermostats at
Grainger are 200 + dollars. ( they do have some that are a little over
50 dollars. )
Dan
Youre going to spend close to that regardless of what 2 stage
programmable stat you go with. . If you want to go the cheap route,
then your outdoor stat idea would be better than nothing.
------------------------------------------------
The Honeywell 2 stage stat I posted( Honeywell FocusPro 5000
TH5220D1003)
is
around $50 and will do the job. It will be less expensive and less of
a
PITA
than running new wires and buying another stat and OD temp sensor that will
support balance point operation.
Well, if he can get a 2 stage stat for $50 , then absolutely that is
the way to go. Ive never seen one that cheap.
--------------------------------------------------
There is a reason I posted that particular model.... Its a good quality
stat, and my customers that have them have been very pleased. You can do a
simple search on yahoo and find a bunch of places that have them for $50 or
less.
It also has an auto-changeover feature.... will change from heat to cool
or
vise versa on its own... nice to have in the fall and spring when your
running the a/c during the day and heat at night.
I personally think an auto changeover feature on a thermostat for
residential is not a good idea ; it could turn on the a/c in cold
weather and possibily destroy the compressor if there exists
interally generated heat from cooking, many people in the house at one
time, or from a lamp too near the thermostat. Id only go with auto
changeover if there was a low ambient cutout switch on the a/c unit.
---------------------------------------------------------------\
Think 5 degree dead band....
I have been putting in both the FocusPro and the VisionPro for many years...
I have never had a problem with compressors. But then the refrigerant charge
is properly balanced by subcooling and superheat, correctly sized ductwork,
etc.
The only way I can think of that you would have a problem with the a/c
trying to come on in the winter is if the stat is in a closed kitchen when
your doing holiday cooking.... not a good idea
A 5 f. dead band is not adequate protection ; if the heating
setpoint is low like at 65 f. the sun hitting the thermostat
directly or a wood burning fireplace , prolonged oven cooking,
etc...could easily push the temperature to 71 f and higher which would
trigger the mechanical cooling at an outdoor temperature cold enough
to cause equipment harm . Shutting off the a/c breaker is always a
good idea in the winter , regardless .


---------------------------------------------------


The 5 degree deadband is a *MINIMUM*... it will not get any closer than 5
degrees. Normal settings are 76F for cooling and 70 for heat. If you drop
the cooling below 75F, the 70F set point will drop accordingly. likewise, if
the heat set point is raised above 71F, the cooling setpoint will rise
according also. When I program a control, the customer will *NOT* be able to
get the set point temps any closer than 5 degrees. I also set the
temperature stops in the control so it will not go below 70F in cooling, nor
above 75F in heating modes.

Its only common sense......and actually reading the directions.
Bruce Murray
2019-02-11 13:33:52 UTC
Permalink
Forgive this newbie question please.
On a 2 stage thermostat, the second stage will kick in if the target temperature cannot be reached with the first stage running.

My question is how does the thermostat realize that the target temp will not be reached?
I suppose it could be done after a certain time delay or perhaps it measures the rate of temperature increase, or maybe a combination of these two.
I imagine there are fancy algorithms used by various manufacturers and I am particularly interested in those made by Honeywell such as the TH6320.

Thanks for your enlightenment.

MLD
2011-12-27 19:44:06 UTC
Permalink
Post by d***@krl.org
My LPG furnace developed a heat exchanger leak and so it has been
replaced with a high efficiency two stage furnace. The old furnace
was also a high efficiency furnace but just a one stage 100k BTU/
hour. The replacement is a 90k btu/hr / 63k btu/hr. Did not do a
proper analysis of the size furnace needed, but based on how the new
furnace seems to be working, the low stage is good to below 20 degrees
F. right now. And I am going to put in more insulation so things
will change a little. The new furnace has jumper settings for using
a one stage thermostat with 5 or 12 minutes wait before kicking in to
high, or for using a two stage thermostat.
Okay here is the question...........it seems to be that the furnace
ought to run at the low stage unless the outside temperature is below
about 20 degrees F. Then switch to high stage as long as the outside
temperature is below 20 degrees. There is no mention of doing this in
the furnace manual. So is this a bad idea for some reason.
It seems like a simple thermal switch located outside would be better
than spending a bundle on a two stage thermostat.
Dan
Bit confused on just how your furnace works---didn't know that any of them
new anything about the outside temperature.
The way that my 2 stage works is pretty simple---When there is a call for
heat it runs on the 1st stage (I think it's about 70% of the furnace's
capacity) and low fan speed for the first 10 minutes. If the thermostat
still calls for heat after the 10 min. then the 2nd stage kicks in and the
fan speed ramps up to 100%. On very cold days the house maintains a fairly
even temperature because the furnace kicks on very frequently and most of
the time cycles only on the 1st stage.
MLD
i***@gmail.com
2011-12-28 15:41:12 UTC
Permalink
Post by MLD
Post by d***@krl.org
My LPG furnace developed a heat exchanger leak and so it has been
replaced with a high efficiency two stage furnace.  The old furnace
was also a high efficiency furnace but just a one stage 100k BTU/
hour.   The replacement is a 90k btu/hr /  63k btu/hr.  Did not do a
proper analysis of the size furnace needed,  but based on how the new
furnace seems to be working, the low stage is good to below 20 degrees
F.  right now.  And I am going to put in more insulation so things
will change a little.   The new furnace has jumper settings for using
a one stage thermostat with 5 or 12 minutes wait before kicking in to
high, or for using a two stage thermostat.
Okay here is the question...........it seems to be that the furnace
ought to run at the low stage unless the outside temperature is below
about 20 degrees F.  Then switch to high stage as long as the outside
temperature is below 20 degrees.  There is no mention of doing this in
the furnace manual.  So is this a bad idea for some reason.
It seems like a simple thermal switch located outside would be better
than spending a bundle on a two stage thermostat.
Dan
Bit confused on just how your furnace works---didn't know that any of them
new anything about the outside temperature.
 The way that my 2 stage works is pretty simple---When there is a call for
heat it runs on the 1st stage (I think it's about 70% of the furnace's
capacity) and low fan speed for the first 10 minutes.  If the thermostat
still calls for heat after the 10 min.  then the 2nd stage kicks in and the
fan speed ramps up  to 100%.  On very cold days the house maintains a fairly
even temperature because the furnace kicks on very frequently and most of
the time cycles only on the 1st stage.
MLD
In residential, its only Heat Pump resistance heaters that are
sometimes enabled/disabled off of outdoor temp. --- high efficiency
gas fired furnaces are not...BUT, it is possible to modify such a
system to accomplish it. The OP is asking if it would be beneficial
for him to do it off of outdoor temp. since he accurately knows that
first stage is good down to about 20 f. for his application ; he
could very easily do it this way...but its not going to be the most
economical . On your furnace....you are using a single stage
Thermostat in conjuction with the 10 min. Time Delay feature of the
furnace to bring in 2nd stage . In my opinion, 10 min. isnt long
enough but you cant do much about that --- youd see better economy
if you had a true 2 stage Thermostat operating the furnace off of
true space demand and eliminating any time function . Of...if you
were proficient , you could at least increase the 10 minutes to 20
minutes by wiring in an independent 20 minute Time Delay Relay for 2nd
stage function, and keep your Single stage thermostat.
danny burstein
2011-12-28 16:04:44 UTC
Permalink
Post by i***@gmail.com
In residential, its only Heat Pump resistance heaters that are
sometimes enabled/disabled off of outdoor temp. --- high efficiency
gas fired furnaces are not...BUT, it is possible to modify such a
system to accomplish it.
our high efficiency natural gas unit ("Lochinvar") has some
sort of internal logic programming that modulates the flame
performance. There's "zero", of course, and then 15 or so percent
and up.

- I don't quite know the algorithm but it measures the outdoor
temperature, and also the delta between the outgoing hot water
and the incoming cooler pipes.

- when first installed the outdoor sensor was wired wrong, so
the unit only fired up to the lowest setting... So it was
getting a bit chilly by the by. He came by and disconnected
it until he could get the factory rep on the phone...
--
_____________________________________________________
Knowledge may be power, but communications is the key
***@panix.com
[to foil spammers, my address has been double rot-13 encoded]
i***@gmail.com
2011-12-28 16:51:47 UTC
Permalink
Post by danny burstein
Post by i***@gmail.com
In residential, its only Heat Pump resistance heaters that are
sometimes enabled/disabled off of outdoor temp.  ---  high efficiency
gas fired furnaces are not...BUT, it is possible to modify such a
system to accomplish it.
our high efficiency natural gas unit ("Lochinvar") has some
sort of internal logic programming that modulates the flame
performance. There's "zero", of course, and then 15 or so percent
and up.
- I don't quite know the algorithm but it measures the outdoor
temperature, and also the delta between the outgoing hot water
and the incoming cooler pipes.
- when first installed the outdoor sensor was wired wrong, so
the unit only fired up to the lowest setting... So it was
getting a bit chilly by the by. He came by and disconnected
it until he could get the factory rep on the phone...
--
_____________________________________________________
Knowledge may be power, but communications is the key
[to foil spammers, my address has been double rot-13 encoded]
On a Boiler, it is called 'Hot Water Reset' (from outdoor temp) and
it shifts the Hot Water output temp to a higher value as the outside
temp decreases . For clarification, I was referring to FORCED AIR
Heating Systems when i said in residential applications that its just
Heat Pump electric resistance heaters that are sometimes enabled at a
certain outside temp. value . A hot water systems such as yours is
THE best for comfort as the outside walls of the structure are
getting blanketed with virtually constant heat of varying degree ...
but high efficiency gas Forced Air Heating does a more efficient job
plus a/c, humidification, and air cleaning apparatus can be easily
added to it making it a complete environmental system . Regards.
danny burstein
2011-12-28 17:15:56 UTC
Permalink
Post by i***@gmail.com
certain outside temp. value . A hot water systems such as yours is
THE best for comfort as the outside walls of the structure are
getting blanketed with virtually constant heat of varying degree ...
but high efficiency gas Forced Air Heating does a more efficient job
plus a/c, humidification, and air cleaning apparatus can be easily
added to it making it a complete environmental system . Regards.
I love our hot water system, but with two complaints that
are intrinsic to the design.

a: as you mentioned, it does great for heating but... doesn't
do diddly squat for cooling.

b: It also only has the ability to raise the indoor temperature
a couple of degrees/hr. So if we've been gone for a week
and the house is at 50 or so degrees, it'll take quite some
time to get comfortable.

(For now we've got a neighbor who can usually come by
and kick it on early in the day we're coming back.)
--
_____________________________________________________
Knowledge may be power, but communications is the key
***@panix.com
[to foil spammers, my address has been double rot-13 encoded]
Steve
2011-12-28 21:20:37 UTC
Permalink
[Quote] In residential, its only Heat Pump resistance heaters that are
sometimes enabled/disabled off of outdoor temp. --- high efficiency
gas fired furnaces are not...BUT, it is possible to modify such a
system to accomplish it. [Quote]

OD temp *is* required for balance point changeover on dual fuel systems, but
not for gas furnaces ... high efficiency or not.

Heat pump with resistance heat back-up will run the strips when needed
during defrost cycle so it won't blow snowballs, or if the heat pump isn't
keeping up with the heat loss.... no additional OD temp sensor is needed or
required. FWIW, Rheem heat pumps have sensors built in that will shut down
the heat pump and energize strips only when the OD temp drops below 6F.
i***@gmail.com
2011-12-29 14:43:41 UTC
Permalink
Post by Steve
[Quote] In residential, its only Heat Pump resistance heaters that are
sometimes enabled/disabled off of outdoor temp.  ---  high efficiency
gas fired furnaces are not...BUT, it is possible to modify such a
system to accomplish it.  [Quote]
OD temp *is* required for balance point changeover on dual fuel systems, but
not for gas furnaces ... high efficiency or not.
Heat pump with resistance heat back-up will run the strips when needed
during defrost cycle so it won't blow snowballs, or if the heat pump isn't
keeping up with the heat loss.... no additional OD temp sensor is needed or
required. FWIW, Rheem heat pumps have sensors built in that will shut down
the heat pump and energize strips only when the OD temp drops below 6F.
When Carrier air to air Heat Pumps were in their infancy, many of the
installations operated with OD thermostats enabling the resistance
heaters to operate in conjunction with the Outdoor Unit during
normal operation . I still have the training material from that time
depicting this.
Daniel who wants to know
2011-12-29 05:08:45 UTC
Permalink
In residential, its only Heat Pump resistance heaters that are
sometimes enabled/disabled off of outdoor temp. --- high efficiency
gas fired furnaces are not...BUT, it is possible to modify such a
system to accomplish it. The OP is asking if it would be beneficial
for him to do it off of outdoor temp. since he accurately knows that
first stage is good down to about 20 f. for his application ; he
could very easily do it this way...but its not going to be the most
economical . On your furnace....you are using a single stage
Thermostat in conjuction with the 10 min. Time Delay feature of the
furnace to bring in 2nd stage . In my opinion, 10 min. isnt long
enough but you cant do much about that --- youd see better economy
if you had a true 2 stage Thermostat operating the furnace off of
true space demand and eliminating any time function . Of...if you
were proficient , you could at least increase the 10 minutes to 20
minutes by wiring in an independent 20 minute Time Delay Relay for 2nd
Post by i***@gmail.com
stage function, and keep your Single stage thermostat.
Or if you just want to be geeky, use 2 single stage thermostats, the first
between R and W1 as per normal the second between W1 and W2. Set the first a
couple degrees higher than the second, so that as long as the first stage is
enough to keep Tstat 1 satisfied stage 2 never runs, if stage 1 can't keep
up the temp drops and the Tstat for stage 2 kicks in.
d***@krl.org
2011-12-29 21:55:19 UTC
Permalink
Post by MLD
Bit confused on just how your furnace works---didn't know that any of them
new anything about the outside temperature.
 The way that my 2 stage works is pretty simple---When there is a call for
heat it runs on the 1st stage (I think it's about 70% of the furnace's
capacity) and low fan speed for the first 10 minutes.  If the thermostat
still calls for heat after the 10 min.  then the 2nd stage kicks in and the
fan speed ramps up  to 100%.  On very cold days the house maintains a fairly
even temperature because the furnace kicks on very frequently and most of
the time cycles only on the 1st stage.
MLD
I am no expert, but do know that some hot water furnaces do have a
sensor for outside temperature and adjusts the flame based on the
outside temperature. In my case i was thinking of just a switch
controlled by the outside temperature . And use that to switch the
furnace to high heat when it is really cold outside. That is not
mentioned in the furnace manual, but seems like it would work nicely.


Dan
Tony Hwang
2011-12-31 23:05:07 UTC
Permalink
Post by d***@krl.org
Post by MLD
Bit confused on just how your furnace works---didn't know that any of them
new anything about the outside temperature.
The way that my 2 stage works is pretty simple---When there is a call for
heat it runs on the 1st stage (I think it's about 70% of the furnace's
capacity) and low fan speed for the first 10 minutes. If the thermostat
still calls for heat after the 10 min. then the 2nd stage kicks in and the
fan speed ramps up to 100%. On very cold days the house maintains a fairly
even temperature because the furnace kicks on very frequently and most of
the time cycles only on the 1st stage.
MLD
I am no expert, but do know that some hot water furnaces do have a
sensor for outside temperature and adjusts the flame based on the
outside temperature. In my case i was thinking of just a switch
controlled by the outside temperature . And use that to switch the
furnace to high heat when it is really cold outside. That is not
mentioned in the furnace manual, but seems like it would work nicely.
Dan
Hmmm,
That does not make sense. Buildings have different air tightness and
insulation. Monitoring outside temp. won't do much for any thing. For
humidity, Yes but temp., No. Furnace will do it's own thing depending on
demand from 'stat.
Loading...